Feature Request: Dynamic Max Modulation Control for OpenTherm Thermostat
Hi everyone,
I'm using the Netatmo Smart Modulating Thermostat with an OpenTherm boiler and I've discovered a significant issue that causes short cycling (boiler turning on/off in cycles under 30
seconds).
The Problem
The Netatmo thermostat always sends max_modulation = 100% to the boiler and only adjusts the water temperature setpoint. This works well for large heat demands, but during low demand
periods, the boiler:
- Fires at full power
- Quickly reaches the setpoint
- Shuts off
- Repeats every 20-30 seconds
This "short cycling" reduces efficiency, wastes energy, and causes premature wear on the boiler.
My Testing Results
I tested different max_modulation levels using an OpenTherm Gateway:
┌────────────────────────┬─────────────────────┐
│ Max Modulation │ Short cycles (<30s) │
├────────────────────────┼─────────────────────┤
│ 30-40% │ 0% │
├────────────────────────┼─────────────────────┤
│ 50% │ 7% │
├────────────────────────┼─────────────────────┤
│ 100% (Netatmo default) │ 15% │
└────────────────────────┴─────────────────────┘
Feature Request
Could Netatmo implement dynamic max_modulation control based on heat demand?
For example:
- Demand ≤ 0.5°C → max_modulation 30%
- Demand ≤ 1.0°C → max_modulation 40%
- Demand ≤ 2.0°C → max_modulation 50%
- Demand > 2.0°C → max_modulation 80-100%
This would completely eliminate short cycling and significantly improve energy efficiency for all OpenTherm users.
Does anyone else experience this issue? Please upvote if you'd like to see this feature!